pls give proper discription of selection of transformer
based on particular load.
Answer Posted / bala_vlsi
first u finalized the connected loads and u will consider
diversity factor for individual loads . after this
calculation u will have some load in kw .
now u will convert to KVA
KW/ POWER FACTOR = KVA
Now you can select the suitable transformer for your
desiarable loads
| Is This Answer Correct ? | 1 Yes | 0 No |