what is the function of Droop CT and where it is used?
Answer Posted / l.l
Droop CT is used to control load sharing of the reactive
power between paralleled generators. Its output is mixed
with the phase voltage to result in a signal that will be
proportional to the lagging power factor. This is used to
adjust the excirtation current accordingly so that the
proportion of reactive power is shared between them.
| Is This Answer Correct ? | 75 Yes | 3 No |
Post New Answer View All Answers
what is the working principle of a DG Set, Alternator, & exiter
how test transfomer(3 phase75kva) by megger
if a 3phase 100kva distribution transformer , 400 v,50 hz, 4-wire system is loaded at 160 k.w mostly 1-phase Lighting & Airconditioning split a.c load what will be the net effect on the power system in terms of voltage, powerfactor, current , efficiency of xformer
How is the gain affected by the introduction of feedback in a control system.
how the testing of protection CT Testing done through Primary injection kit please describe in detail procedure...
WANTCONTACT NUMBER & EMAIL/ WEBSITE TO CONTACT THE SECRETARY,MADHYA PRADESH LICENSING BOARD(ELECTRICAL),K- BLOCK,3RD FLOOR,SATPOODA BHAWAN,BHOPAL
How many methods use the load flow solution?
What are the functions of temperature scanner in power transformer?
What is electrical cable termination
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
explain the process of commutation in a dc machine. Explain what are inter-poles and why they are required in a dc machine.
can anyone show me how the 3 phase power is supplied to socket outlets?
What are the types of instrument transformer?
How to calculate loses in transformer of 160 KVA ?
What are the main parts of central chiller plant? Explain the function of each stage.