What is Energy based relay coordination & time based relay
co-ordination? In which type of distribution arrangement
these methods are applicable?
Answer Posted / omar aziz
Every electrical equipment installed in a power system has
an I2t rating. Eg(20kA for 1sec) This indicates the maximum
permissible energy that the equipment can withstand before
blowing into bits. Protection co ordination must ensure
that this damagiong curve is always protected by the
protection system. This is Energy based coordination.
Time based coordinaation is when no energy basis are
required but time selection is picked for personnel safety
reasons and not equipment damage reasons
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Write the analogous electrical elements in force voltage analogy for the elements of mechanical translational system.
state types of reflectors in illumination engg. ???????
Why do we perform an open-circuit test and short-circuit test on the transformer?
Why we use circular(Stepped) cross section in transformer core?
What is difference and reason b/w -48V BTS system and 24 V BTS system. Plzzzzzzzzz tel me.
what is the meaning of neutral displacement ???
(1)Can earth and be conected together (2) what is the diferent between earth & neutral
Please explain me about Relay curves and their sources to read ?
Define cut-off rate?
how to changeover ups in this power failur time?
What do you mean by passive circuit elements and why these are called passive?
what is the ground fault relay,which purpose it will be use,clearly tell me plz
How PADO software increase the efficiency of power plant?
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
What is the armature mmf in a D.C machine?