Answer Posted / upendra sharma
Neutral displacement relays are used for capacitor banks,
theses realays protect system against imblancing of
capacitor bakns. Application of these relays are wye
connected ungrounded banks. relay detemines the gravity of
imbalance and isolate the bank in case of faulty capacitor
of any phase.
| Is This Answer Correct ? | 7 Yes | 1 No |
Post New Answer View All Answers
what are the dimensions for 200 kva transformer plinth (plateform),in which pcc m20 is used..
Can you used moeller lzm1 mccb in a dc system with 125vdc and 20ka short circuit current , beside is it have 24 or 48 volt shunt ? Beside how long current can through from An MCB shunt contacts? (like Z7-AS 24 V)?
With a phasor diagram show the effect of increasing the field current of a generator supplying a constant real power and connected to a grid system.
Initially, when the input is not equal to the output — what type of response is this?
(1)Can earth and be conected together (2) what is the diferent between earth & neutral
Name the types of motors used in vacuum cleaners, phonographic appliances, vending machines,refrigerators, rolling mills, lathes, power factor improvement and cranes.
How many sprinklers should be in one pipe line?
what r substations?what r there work?why voltages r incresed and then reduced during distribution of power
What is transient response?
Why do we use copper cable for HT Supply and why not Aluminium?
what is a reactive power? what is the relation with power factor?
Why do we pefer VCB over OCB?What are the advantages of VCB over OCB?
how to decide no of electrodes for 1600A LT Main incomer panel
In india, according to trade theory above 5 HP motor reqired star delta starter. But we R connect 11 KV motor with 14MW in Direct to line ( With VCB starter combination) Can U Guess, How it is possible ?????
Both generator parallel condition shared load equally but one genrator taking ampere more than the other what are all the causes to make like this