different between circuit breaker & switchgear & relays
Answer Posted / maheskumar
relay is an protecting device it protect only an particular
connected line
circuit breaker mostly used in transmission so it protect
against high voltage line any fault contition circuit
breaker trip the line and protect the device
switch gear it can be used to prodectbusbar with many input
and outputs
| Is This Answer Correct ? | 5 Yes | 5 No |
Post New Answer View All Answers
How is the percentage impedence of a transformer fixed at design stage???
can indirect loading be called as phantom loading?
What happens when ac supply is given as excitation voltage instead of dc supply
how is the magnetic current test is different in delta-star and delta delta transformer.
a 230v transformer with step down ratio 19:1.it has 2000turns on primary and rated 25va calculate max primary current no of secondary turns volts/turn
difference bewteen reverse current and alternating current
What is creepage distance..... what will be the value for different voltage level
Explain Even and Odd signals?
If a transformer primary winding operates at 240v, the secondary at 120v and the load is 1500w & the transformer is rated at 92% efficient, what's the current flowing through the primary winding of the transformer? What is the formula for finding this?
how to conduct dc resistance test for rotor of an alternator and how to measure the rotor dc resistance value theoritically?
In the formula : Knee point voltage = Burden X alf / class, Please inform what is alf? regards Shashidhar M.R.
whit is 33kv power 300*300 cable full current with formula
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
I'm looking for a softcopy manual set for a Credence ASL- 3000. Anyone know where I can get it?
What Maximam Gap Taibaar & Bush