In transformers Which type of connection is preferred for
harmonics to be minimum.
primary : secondary
star without neutral:open delta
star with neutral :open delta
star without neutral: delta
star with neutral : delta
explain why
Answer Posted / sudheer868
ANS is star with neutral and delta.For harmonics effect to
be minimum we must provide a closed path for harmonics in
phases so that they circulate only in phases and does not
enter into line.Hence harmonic effect is less in delta
connection than in star connection.In star star connection
ti provide closed for harmonics neutral is grounded
| Is This Answer Correct ? | 1 Yes | 1 No |
Post New Answer View All Answers
How many wall/floor flange will i use in bus duct system if we have in our design a 35th floor building.
why do motors burn out? I understand why adding parallel loads to a power source means more current moves through the circuit, and can destroy circuit elements by overheating. What about when you have a vaccuum cleaner intake flush against a floor, a room fan sitting directly against a wall, or a power drill trying to drill through something too hard?
what is the difference b/w pvc cu conductor and cu breaded wire..?
what are problems caused by the pdu in rack server
how can i determine the KVA/MVA rating of transformer precisely?? is there any standard test?????
what is smart grid? why we use it? explain in detals bcoz i want give presentatin from it....
how circuit breaker work.. what is the operations taking place inside a circuit breaker when an overcurrent occurs... is it similar to fuse?
What are steps to be taken while designing of DYN11 distribution transformer to achieve magnetising balance?
for hipot test on 33kV busbar, we will test on 70 kV or 56kV, what is the acceptable leackage current?
How to check the cable fault / hv test of transformer cable.
what is doid
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
how to differentiate a mpcb,mcb with a contactor? Explain their working operation
What is lighting kitts.
size of condotory fron voltage level