different between circuit breaker & switchgear & relays
Answer Posted / tareq harb
relay ca be used to protect against one fault at a time
either overcurrent or undervoltage or underfrequency but
not together, can also be used in switching & control
systems.
Breakers can be used to protect againt too many abnormal
faults in the circuit at one time.
switch gear is a series breakers connected to gether to
form a complete protected bus bar with many inputs outputs.
Is This Answer Correct ? | 33 Yes | 4 No |
Post New Answer View All Answers
Draw transformer phasor diagram.(full load,no load)
Why is the frequency not changed during transformation of electrical energy in a transformer?
why transformer ratings in kva? & DG ratings in kva? & Motor ratings in kw/HP?
Why High voltage are generate noise ?
In the N-series schneider reclosers. What is the difference between current during fault time and current at tripping? This appears in the Event log in an event of a trip out.
how much cable size required for 70 kilowatt load.
What is difference between start imitation and start interlock for 3 phase motor protection ?
battery capacity use of made?
what exactly commisioning work does in electrical site work... LT side?..
differnce between single acting and double acting solenoid valves
why capacitive load is not used in routine life????any reason is there ??????
How can maintain our H.T. motors used in cement plant. please send me procedure.
What are the reasons for the parallel operation of transformers?
How you give clearance to a spare feeder.
How to Decide the Location of Earth pit for Compressor in Oil Depo? and How to measure the resistance of earth pit Pls explain me with the help of Circuit Diagram?