if we increase the frequency given to a transformer then wat
will happen to the transformer size, whether it will increase?
Answer Posted / amir rashid chishti
If we increase the frequency then transformer size will
reduce so it will not increase. In electronics circuits we
often see very small transformers due to high frequency
whereas in power systems we have large size transformers
due to low frequency.
Hope answered the question!
| Is This Answer Correct ? | 13 Yes | 2 No |
Post New Answer View All Answers
What is the operating principle of turbo-generator.
what is a reactive power? what is the relation with power factor?
ROC converges if pole and zero lies inside a) origin b) z=1 c) pole d) zero ? Explanation please? if ROC does not converges then?
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
Whats the minimum value for I.R. that can be allowed for HT & LT alternators for operation?
What do you mean by power transformer?
1.main parts of generator? what is used A-check,B-check,C- check? 2.what is FM200 system in data centers? 3.difference between pac,ahu?
please explain how to do 'pole drop test' on generator?
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
how to compare with Relay settings for HT< panels, RMU panel, and PSS CSS transformer?? 1) Load amps, 2)Tripping time, 3) CT ratio, 4)Cable size 5) Transformer KVA rating 6) transformer full load amps
How much no load current of synchronous motor
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
Did RMU have ct and pt ?
Mention the disadvantages of low power factor? How can it be improved?