How many earthings are required for commissioning the
Transformer?
Answer Posted / easa paul
4 nos.(2 are for Body earthing and another 2 are for neutral earthing).
| Is This Answer Correct ? | 9 Yes | 1 No |
Post New Answer View All Answers
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:
What is BusBar integrity test and how it is conducted?
How to calculate capacitor bank size at a load 800kVA.
is there any chart showing the suitable cable size according to AMP and length ? for three phase motors
anyone knows service engineer in chennai for EDM SPARKING MACHINE.CHMER PULSE CD 60 M.pL GIVE ANY CONTACT NOS
11 kV line deraction check by an Engineer.
What is referred to the electron in the outer orbit?
why on delay timer used for fully automatic star delta starter?
Define phase cross over?
What is difference is of VSD,VFD,VSDS, are they the same as the direct current to control dc using above mention
What are the Full Forms of TVM, MTL, CVT ?
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?