if we convert ampers into kw,which one formula use by
us,pls tell me?
Answer Posted / pillay
there is no one formula only.
there are some formulas that you must know,,
you must know how to use the correct one when you need it.
for DC power it is always just voltage x current = watts
for AC single phase it is always volt x current x pf = watts
for AC 3 phase it is root 3 x volt x current x pf = watts
the watts than you change to KW or MW if necessary.
this are all for real calculations. when you practice with it often than you will be able to give an estimate bcos the pf varies according to situation.
Is This Answer Correct ? | 6 Yes | 0 No |
Post New Answer View All Answers
Which type of DG need Netral Earthing?
What is the dependency of stiffness on load angle??
How you will determine the volume of oil in a particular Distribution transformer.
What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?
What is cathode ray oscilloscope (cro)?
How to calculate no of EARTH PIT? Describe the formula as per IS standard?
when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?
what is the effect of un-synchronized power.
why is control bus bi-directional?
Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.
What are the transformer losses?
why motor range is available 22kv,30kv,37kv,45kv and so on? why motor range is not available 21kv,24,25,26,27kv and so on?
300m long and 30kw inductive loade 3phase supply how many size cable required
what material is used in capaciter