if we convert ampers into kw,which one formula use by
us,pls tell me?

Answer Posted / pillay

there is no one formula only.
there are some formulas that you must know,,
you must know how to use the correct one when you need it.

for DC power it is always just voltage x current = watts

for AC single phase it is always volt x current x pf = watts

for AC 3 phase it is root 3 x volt x current x pf = watts

the watts than you change to KW or MW if necessary.
this are all for real calculations. when you practice with it often than you will be able to give an estimate bcos the pf varies according to situation.

Is This Answer Correct ?    6 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Which type of DG need Netral Earthing?

4508


What is the dependency of stiffness on load angle??

834


How you will determine the volume of oil in a particular Distribution transformer.

1443


What is the typical enclosure type used for Indoor switchgear / Outdoor switchgear Units? - In Onshore / offshore Units?

536


What is cathode ray oscilloscope (cro)?

679






How to calculate no of EARTH PIT? Describe the formula as per IS standard?

1580


when we have to use UPF wattmeter and LPF wattmeter? what is the difference between UPF and LPF wattmeter in terms of construction?

1928


what is the effect of un-synchronized power.

1547


why is control bus bi-directional?

1711


Trafo ratio is 11kV/6.6kv,Vector group is YND11. What will be the effect if secondary is used for earthed system.

3350


What are the transformer losses?

678


why motor range is available 22kv,30kv,37kv,45kv and so on? why motor range is not available 21kv,24,25,26,27kv and so on?

2364


300m long and 30kw inductive loade 3phase supply how many size cable required

1000


what material is used in capaciter

1474


how you configure motorvision relay (L&T make)from DCS

4329