megger how much voltage will produce ?

Answer Posted / pswin

It will depends on the type of magger. You can choose desire volt by using selector switch within the range of magger. For low voltage switchboard busbars, 500 V is enough.

Is This Answer Correct ?    5 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Why need 3phase machine double earthing?

1429


i have install 750 kva distribution transformer at my site and want to do neutral earthing. what calculations should i follow to determine earthing conductor material and size?

1668


Dear sir, my knowledge about cable size determination is limited. Though I read examples I could not calculate the Cable size required for electric driven pump 40 KW, 380 Volt, 50 HZ, 50 meter from transformer and it is three phase star delta starting. Please help as there is no one in my surroundings to help.

1396


If VFD is On but no starting commond on it. so how many outpout voltages of VFD

796


What is the physical significance of phase.. i.e. what is exactly the meaning in layman's language.. 1 phase, 3 phase etc ???

1765






what is the need to express current and voltage in rms value? rms value is also called as effective value,what is effective value?

1583


what is meant by directional earth fault and non directional earth fault? describe both.

1559


if field breaker of generator is closed prior to its rated speed on a power generating unit. what will be the effect on generator, unit transformer and starting transformer.

1384


what is basic difference betmeen normal & flame proof motor??

1735


why using transformer and thyristor switch in 3 phase apfc panel

2488


what is maxemo work permit procedure

1792


how will we calculate the copper wire load..

1550


I want to design a heating coil of 80/20 nicrome for 3.5KW please give me the calculations choosing for physical dimensions assume coil voltage will be 110V AC assume necessary conditions

1289


I have one ct of ratio 3000-2000/1 Amp its knee point voltage mentioned on name plate is 500-333/30mA-50mA at Vk/2. in secondary box there is three terminal named 1S1, 1S2, 1S3 then on which terminal obtained the knee point voltage ie 1S1-1S2 OR 1S1-1S3 & also specify the knee point voltage for the ratio 3000 from name plate.

2093


please send the last 5 years {{{JUNIOR ENGINEER - ELECTICAL, ELECTRONICS RRB CHENNAI and secundrabad}}} TECHNICAL question papers TO MY EMAIL ID dinesh100701@gmail.com

1803