A heater capacity is 3.0 KW on 415V . if supply voltage is
380Volt . what is heater capacity on 380volt . and how
calculate and give formulas . Prakash veer singh
Roto power Engg.
Answer Posted / anil patel
1. Given v= 415v
kw= 3w
formula = w=v*v/R
3000=415*415/R
R=172225/3000
R=57ohm
I=v/R
I=415/57=7.28amp
2. given v=380volt , kw=3
R=380*380/3
R=48.133
I=V/R
=380/48.133
=7.8 amp
| Is This Answer Correct ? | 5 Yes | 7 No |
Post New Answer View All Answers
What is float cum boost charging system?
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
Please define ampere?
What is inverse definite minimum time lag relay? Where is it use?
Which type of DG need Netral Earthing?
what is doubling factor in making current of a breaker?
how can i get an electrical c-certificate?
what is the defination of Cable database? What are the points are considered while preparing cable database? Is there any sample available for cable database?
where can i get vijaya electricals limited in hyderabad interview auestions can u give me the website address plz
How the PF control while running DG set with load
How you will determine the volume of oil in a particular Distribution transformer.
What is the current carrying capacity of 35sq.mm flexible cable?
What is the difference between electrical earthing and electrical grounding?
Why do not we prefer non conventional sources of energy to conventional sources?
What are the basic & Majour problems in UPS ?