can you give main difference between ELCB And RCCB?
Answer Posted / manas
ELCB-- earth leakeage circuit breker
RCCB-- residual current circuit breaker
MCB -- minuate circuit breaker
ELCB-- for earth leakage protection
RCCB-- residual current protection
MCB-- overload protection
ELCB
when leakage of current from phase to earth occurs than
it operate
RCCB
it operate when there is a difference of current between
two phase.
MCB
it operate when there is a overload occures
practically
RCCB=ELCB+MCB
| Is This Answer Correct ? | 23 Yes | 9 No |
Post New Answer View All Answers
Is Transol transformer oil comparable to nynas nytro libra?
how many parameters can integrate with fire alarm basically ?
what is the relationship between current&voltage in practical purpose ?
what is the role and fuction of automatic transfer switch in rotary ups
What is the technical difference between On delay timer and a Star delta timer?
what is mean by restructuring power system?
what are all types of cross section in AC cables?
from which subjects most of the technical que will b asked for hpcl(electrical).pls help me
what happen as when voltage drop(or may decrease) ? in case of atomic base theory?
exolain the star delta connection
Which motor is 3.3 or 11kV more reliable, in terms of efficeancy,maintenance, reliability.
How we can change the direction of rotation of Induction motor? Prove it using graphical
How to dimensioning SDCCH, LAPD and CS7 signaling on GSM?
Should power factor be low or high?
in a simple IDMT relay we use neutral point of ct for earth fault then what is the requirement of neutral ct and cbct?