what are the effects on an power plant and consumers if the
power factor is increased or decreased?
Answer Posted / sushil
increase in power factor gives reduced current, thus
reduced load, increased frequecy,thus reduced input
consumption per unit power on power plant. for decrease it
will be vice-versa.
For consumers increase in power factor reduces penalty or
reward in the form of decrease in bill.
| Is This Answer Correct ? | 10 Yes | 1 No |
Post New Answer View All Answers
what is the difference between surge protection capacitor and surge arrestor
how make megger test for control cable like 12c x 1.5mm and what it apply voltage and test timing details.
What should be the magnetic balance test values for a 3 phase delta/star connected single primary dual secondary winding transformer (90 MVA / 2 X 45 MVA TRANSFORMER)
IF HT CAPACITOR IN ON POSITION IS THERE ANY LOSSES I.S I SQURE OCCURS IN THE SYSTEM
What is mean by hot and cold loop testing?
Hello sir, pls send me hpcl technical test papers .i am. Appearing for the exam.
why we are not giving the zone 1 trip command to the master trip relay
In single phase ac ups supply when current is measured with tong tester neutral current is found more than phase current.What is the reason?
Please define ampere?
in what type of applications v can use q meter?
Can an inverter be used as a converter? How?
can i able to get bhel previous exam question paper?
can a 150 kva 3 phase 440v/230V delta-wye step down transformer can be use as step up transfoermer with connected loads at 440v side?
When steam condenses and becomes water at the same temperature, the specific heat for the process in kJ/kg k is
main difference between ac and dc?