how can we change the rotating direction of single phase AC
induction motors?
Answer Posted / raghunandan
as single phase Ac induction motor are not self starting
they need capacitor to introduce phase difference.In
capacitor start and capacitor run motor(all ceiling fans) by
interchanging the leads of either capacitor or running
winding we can change the direction of rotation.
| Is This Answer Correct ? | 48 Yes | 10 No |
Post New Answer View All Answers
Has someone here done a sizing for a generator (3 phase), its for a pumping station. If you have an example for standby/duty and both running (I) star delta (ii) Soft Starter.
Define availability (operational)?
The series field winding has low resistance while the shunt field winding has high resistance. Why?
Can you please explain creepage distance in detail, for a 6.6kV cable head what must the distance be and how do you determine it?
I am having a 1500 KVA transformer whose secondary current is 2086A and my connected load is 1000 KVA, I am having 400 KVAR APFCR for PF improvement what ratio of CT should i install in LT EB Bus to get optimum PF improvement?
induction 3 phase motor terminal connection
it is possible to measurement of tension of slipring induction motor(SRIM)carbon brushes, any maesuring instruments are available in the markets.
how slip power recovery system work
State kirchoff current law?
How to findout raw or ups power? its not indicated in socket,
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
In convertor can we use rectifier thyristor in place of invertor thyristor with explain.
Why neutral is not used in three phases dol starter
What is a single phase autotransformer?
what is gas turbine intercooling ?