what are the types of Distribution transformer vector group
please explain
Answer Posted / amit3456
vector group shows the phase shift between winding, if it
is yndn11 it means primary is star and secondary in delta
and since the difference between star and delta is
30degree, so 360 is divided by 30 deg, it will divide in 11
posn.
| Is This Answer Correct ? | 8 Yes | 6 No |
Post New Answer View All Answers
Why the field rheostat is adjusted such that the voltmeter reads 380V
What is open loop and control loop systems?
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
WHAT WOULD BE THE FORMULA OF WIRE GAUGE FOR A FULL LOAD CURRENT
In HI POT test what is reason for applying the AC VOLTS and DC VOLTS in different applications what is the nessesity for this ?
how electrical earthing maintenance done in industry?
we have 2.2kw,Y,3000rpm motor but 6leads found in TB what happen if we connect in delta?
Disadventage of cable-gland earthing if any ?
What is the difference between Generator Differential Relay and Transformer Differential Relay?
Why Water motor is not taking a load or pressure while everything is correct. (Note: Motor running properly)
Initially, when the input is not equal to the output — what type of response is this?
What is the difference between PS & metering CT (5p20,0.5 etc.)? Why in PS class CT only Vk is given ? Is PS class CT is more accurate than metering CT?
Hi, My plant daily consumption is calculated as 3.8MWH but my supplier has sanctioned an power of 2.6MW per day. how can i equal or distinguish this two factors
What are stable systems?
How to maintain ac plant?