What is the function of earthfault relay?
Answer Posted / sennapparajan
The function of earth fault relay is to to protect the
device from earth fault. there are 2 types of earth fault
fault relays
1.neutral ct conneted earth fault relay. it will sense the
current flowing through neutral while earth lerakage.
2.three phase ct's connected earth fault relay.in normal
condition the sum of three phase ct's current in zero.
when earth fault the sum of the 3 phase ct's curret are un
balanced that time relay acts.
| Is This Answer Correct ? | 67 Yes | 7 No |
Post New Answer View All Answers
how to determine the inrush current of a transformer
Why auxiliary transformers are not connected in parallel in primary stations?
What is turn ratio of a transformer?
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
how we control automatic generator i'e with to supply (main supply and local generator) when the main supply was break to supply the local supply automatically to begin supplying power.I now this control circuit is the combination of contactor time delay contactor switch and overload relay .but my question is how we combine those component thank you
How one may guess the direction from which the distribution line is incoming if there is no pole plate on poles?
What current position are you holding in your current company?
How much dc volt applied in cathodic protection system?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating
what is the reactive power what is the use of it in system
What is the magnetic field (coil DC ) of Turbo Expander?
explain different types of d.c motors?
WHAT IS THE FORMULA FOR CALCULATING CURRENT RATING(DIRECT IN GROUND OR AIR) OF ARMOURED(XLPE) CABLE OF 4C,16Sqmm?
IF % IMPEDANCE OF A TRANSFORMER IS INCREASED FROM 5.8% TO 8% HOW MUCH THE EFFICIENCY OF THE TRANSFORMER WILL COME DOWN?
What is hipot test procedure?