What is the function of earthfault relay?
Answer Posted / pratheesh
I agree with Mr.Ravikumar except in one point.
If the load distribution of a 3 phase 4 wire system is not
balanced in all three phases, there will be some potential
in neutral wire and thus a current flow also.
In this condition, if the neutral wire touches to earth
after the earth fault relay CT, definitely this E/F relay
will sense this current flow from neutral to earth and thus
trip the circuit.
If any other disagreement, please mail me at
pratheeshtn@gmail.com.
Thank you.
| Is This Answer Correct ? | 33 Yes | 5 No |
Post New Answer View All Answers
Can i replace Earth leakage relay to the faulty Earth Faulty Relay
How many types of circuit loads are there in a common electrical circuit?
What is the formula for calculating impedance of transformers connected parallel at fault level 50KA?
i am studying in final year can i allowed for 23rd UES of Indian army
why any centrifugal blower draw more current in starting. consider id fan and fd fan?
Basic motor transformer generator
i want to know that what is the eligibility critaria for ongc exam?
Differentiate between induced emf and self inductance?
What is the formula to calculate the rating of a three phase miniature circuit breaker
What is electrical diversity factor in electrical installations?
What is dielectric loss?
For small size, high frequency coils, the most common core material is- a. )Air b. )Ferrite c.) Powdered ion d.) Steel
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
If one lamp connects between two phases it will glow or not?
how to setting voltage RTCC panel