what is pressure relief valve?where it is used????
Answer Posted / jiten
PRV (Pressure relief valve) is one of the protection
component in the transformer. The main purpose of the PRV
is to protect the expansion of oil during any inside fault
of transformer.
During fault this PRV operate and trip the transformer. So
it can be protected from further damage.
| Is This Answer Correct ? | 71 Yes | 2 No |
Post New Answer View All Answers
Is the theorem applicable to ac sources?
What is the theoretical reason for the size of a zig zag grounding transformer to be 1.732 times less than that of a wye-delta grounding transformer used for the same application?
what is W.T?specify the acceptable range?
What is nyquist contour?
What is an order of a system.
What are the types of control system?
before transformer oil dielectric strenght tests are taken the oil should be allowed to settle to remove option 1 air bubbles 2 gasses 3 contamination 4 water
How is operate breaker failure scheme in substation
explain supply side and demand side energy management with advantages & disadvantages
Actually I have a doubt on neutral and earth.we use Ac power without taking neutral by connecting to earth,but at that time does it affects on efficiency of any electrical components or no? If yes how?
What are the types of the glands and difference between single and double compression type of cable Glands.
How to find ampere on ht side for selection of cable size ???
Can anyone explain me about the capacitor calculation
what questions are asked in the interview for the post of an electrical maintenance engineer in FMCG companies?
I want to know the 'Test voltage' for Tandelta testing of 3.3 / 6.6 / 11 KV Motors. Please explain