What is the Difference Between MCCB & ACB & VCB
Answer Posted / kumar t
Mccb is moulded case circuit breaker.
ACB is air circuit breaker.
VCB is vacuum circuit breaker.
MCB is stand for miniture circuit breaker.It is for low
voltages.
MCCB is stand for moulded case circuit breaker. It is for
medium voltages.
ACB is stand for Air circuit breaker.It is for high
voltages.
| Is This Answer Correct ? | 66 Yes | 123 No |
Post New Answer View All Answers
How much voltage we need to apply in 33kv cable during hipot test of cable
what are the steps involved in generator load test?
What is the capacity of the Fastners 12mm?
Advantages of using generator circuit breaker (GCB) scheme in a power station ?
What kind of maintenance is conducted for Transformer
How to work definite,over pluxing,revers power,OSR relay
what is R Core Transformer. how it differs from normal transformers. dont search in net and post the answer.
Explain and give examples about VCB?
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
what is the difference between gas group b and gas group c electrical equipment construction wise?
How to calculate the volumetric capacity of a oxygen & Nitrogen gas Cylinder if pressure is 145 kg/cm2 & water capacity of cylinder is 67 liters.
along with technical test papers
how many stairs have you climbed while you were coming
How seriving & testing of the HT & LT breakers are done. What are the standard Ir values on which we can come to know the test is passed or failed?
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?