Answer Posted / gajanan
star delta starter is used to reduced starting current
taken by motor. for this first startor wdg made connect in
star and then in delta.
| Is This Answer Correct ? | 47 Yes | 2 No |
Post New Answer View All Answers
why 3 phase is converted into 2 phase using electronics circuit why not 2 phases are diresctly putted from the 3 phase transformer??
Why it is necessary to isolate fire fighting when you are taking shutdown for lv board.
ACB & VCB how do work and saftes and how can maintenance in this and parts name show with picture
how generator avr give to the input?
A motor running with lenze frequiency inverter stops if I REDUCE SPEED with 25% load.If I run it in High speed and medium speed running smoothly with full load.please help me to solve it.
Draw the vector diagramme for Asynchronous Induction Generator at noload,half load and fullload.
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
following are the questions asked in interviews: 1) Considering the short circuit fault, which switchgear is preferable, SFU OR MCCB? Which operates faster? whicg one is popular in Indian Market and why? 2)Define SCPD. What is type2 coodination? 3)Why the contactor rating is higher for the fuseless selection than for fuse selection? whether the ratinf of SFU or MCCB remains the same in both the cases? 4)If the HP rating is known then can you calculate the ratings of L.V Switchgear(SFU/MCCB, contactor, OLR) without using the selection chart?
iam using DM 3251 voltmeter(1 percent accuracy)for 11KV system PT ratio is 11KV/110V.can anybody explain what is the max and min voltage deviation.
WHAT IS THE CURRENT CARRYING CAPACITY OF 2.5/3 CORE HI TUFF CABLE,WILL IT SAFLEY CARRY 8.6 AMPS OVER 120 METRES,CAN YOU ALSO ANSWER WITH FORMULA FOR WORKINGS OUT ,THANK YOU 3RDYR APPRENTICE.
STATE WORKING OF VACCUM CIRCUIT BRAKER?
how to calculate the breaking capacity of different breakers.
What type of pipe material G.I or M.S is used for sprinkler system?
how to select automotive wire by mathematical equation with given current, vlotage and resistance
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA