what is the difference between power and distribution
transformer?
Answer Posted / santosh jadhav
power transformers are used in transmission network for
voltage ratings of(440kv,220kv,110kv,66Kv) and are generally
rated above 200MVA.
Distribution Transformers are used in (33 kv,11kv,6.6 Kv
)voltage levels in Distribution network and are generally
rated less than 200 MVA.
| Is This Answer Correct ? | 22 Yes | 73 No |
Post New Answer View All Answers
can anybody sent me power grid questions. what subject should i prefer for preparation?
We have given to 3phase supply to ups system & how can coming netural
any one guide me to reduce the power factor of diesel Generator from 0.97 Leg to 0.8 Leg.with out any change in my load.
how do u gauge the size of the cable ?for eg. consider a 300 sqmm L.T Cable.How do u determine the size of the cable seeing it pratically?
how to calculate
What is the distance between each insulator in 33kv transformer and how can it calculate
my diploma certificate in my higher education college
How much minimum insulation required between 11kv/3.3kv transformer windings?
how a resistor resists to flow the current?how an inductor oppses the sudden change in current?how a capacitor opposes a DC voltage.
What should be the voltage between Neutral and Ground in secondary side of the step down transformer (230 V to 110 V) with no load condition?
IN MY SYSTEM THERE IS ONLY OVER CURRENT EARTH FAULT RELAY IS AVAILABLE. FOR THE UNBALANCE SENSING IS THERE ANY RELAY IS AVAILABLE? THE SAME CTs WHICH ARE USED FOR THE OVER CURRENT EARTH FAULT RELAY CAN USE FOR UNBALANCE ALSO?
what is meant by power and distribution transformer ?
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
why Lightning arrestor are made by 2 seperate stack of inslutor but why cvt are in single stack of insulator.
What does ampere turns shows?