Do you know the overhauling of a motor?
Answer Posted / vijaykumarht
Overhauling means re-conditioning. Dismantling the complete
motor, checking for any damage or wornout parts replacing
the damage or wornout parts(bearings, carbon brushes, end
covers etc if required)and assembling it.
This is done to increase the life of the motor.
| Is This Answer Correct ? | 122 Yes | 14 No |
Post New Answer View All Answers
Give some example of fault limiting devices?
what causes contact chatter when there is no demand on the air conditioning unit?
What is hipot test procedure?
How to design harmonic filter at the project stage without nowing the harmonics levels
What are the no-load losses for the 11000/415V transformer with the following rated capacity? 1.1500 kVA 2. 2000 kVA 3. 2500 kVA 4. 3000 kVA
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
how to find number of run cable laying[LT side] for transformer & alternator secondary side? [above condition for getting output power transformer to main panel side] give the example.
What is q factor?
neutral earth resistance testing is it possible for transformer while in load condition
How would you calculate power loss in a resistor?
I am getting above 60 V as open delta voltage against single phase unit ICT at tertiary delta formed and ICT getting trippped on NDR. ICT tested and found in order. PTs provided on tertiary are tested and in order. what may be the reason?
what is dry and wet frequency withstand voltage? why & where it is used??
what's the exact magnitude of current, flows through Neutral?
What will be the current drawn by HT motor, if low voltage is applied.. any formula to calculate the LT amps of HT motor.?
what are the precuation should be taken ahen installing power transformer,circuit breaker,current & potential transformer