How can we calculate the fault level of the distribution
system knowing the percentage impedance of transformer &
subsequent equipments.
Answer Posted / amar singh.
fault level depend on system impedance
full load current*100
Trasformer fault level= ----------------------------
%impedance of the transformer
| Is This Answer Correct ? | 51 Yes | 17 No |
Post New Answer View All Answers
surge tank, hrc fuse, earthing transformer, firm power objective type
What is the function of attenuator in cro?
why the colour of insultor stack , petticoat is brown. Is it has some technical reason.
What is servo motor? what is its purpose?
why would amp draw on neutral wire be as much as amp draw on the hot leg.
As an electrical engineer what are the responsibilities which i can hold in TCS?
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT-SWITCH BOARD,MLDB,ACB,BUSBAR,ETC,......?
What do you mean by pull of electromagnet?
working of diesel generator ?
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
How work of capacitor in dc supply...???
How to calculate size of HT breaker with the help of Amp (current)? Please provide answers with examples.
What is the types of HT motor testing
Can any body tell gulf interview question for experienced electrical engineer ?
Any one can explaination about calibration with rotating sub standards?