What is the difference between online ups and offline ups?
Answer Posted / hasan
Online UPS is unterrupted power suppy to the load,
Offline UPS can't ensure uninterrupted power supply, it
depends on the tolerance of the load. For any sophisticated
equipment (medical equipment), Online UPS is recommended.
| Is This Answer Correct ? | 59 Yes | 25 No |
Post New Answer View All Answers
What is the relationship between voltage,current & frequency?
what is the efficiency of thyristor
2. Modify your design in question 1.a so that the circuit works according to the following function table X Y F 0 0 Clear 0 1 No Change 1 0 Parallel Loading 1 1 Count 3. Design a circuit that detects the pattern 010 in a serial input X considering: 3.a Overlapping 3.b No overlapping
What is the difference between hot and cold loop testing?
In Electrical 'Single Line Diagram' cable nomenclature shows "2 X 1C X 630sq.mm to be provided for one incomer. The question is how many cable to be proved for one Incomer.
why h parameter are called as hybrid parameter?
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor reactance at stand still is A 2 ohm B 1.25 ohm C 3.15 ohm D 2.25 ohm
what are the condition that makes hooter blow?
how to carried out tan delta test in 11 KV alternator ?
Which device is used for the source of emission of electrons in a crt?
What is the distance between body earthing and neutral earthing.?
why capacitance effect is predominant in underground cable transmission and inductance effect is predominant in over head line transmission?
area control error
How to improve fuel cell in a distribution system?
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?