WHAT INSTRUMENT IS USED TO MEASURE THE MAGNETIC FLUX?
Answer Posted / suresh
Magnetic gaussmeter
Is This Answer Correct ? | 8 Yes | 3 No |
Post New Answer View All Answers
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
Is it possible to make a 5P10/ CT Ratio 50/1A Burden 5VA
Is there any guideline say about display of earthing value near to earth pit
What are the main parts of central chiller plant? Explain the function of each stage.
how many load we can take for lighting
nwhat are the main Components of servo motor?
Define the overload capacity of the motor?
what is the current setting for different relay protection for transformer .
checking procedure of capacitor based motors.used in fans etc?
PLZ SEND ME SOME UNIQUE PROJECT OF ELECTRICAL ENG (B.TECH)
WHY TERTIARY OF POWER TRANSFORMERS IS LOADED WITH EQUIPMENTS LIKE CT,PT,ISOLATOR AND CB
what is p.s impedance measurement test in earthing transformer?
Compare salient pole and cylindrical rotor machines.
What is the difference between vector surge relay (78) and Pole slip relay (98G)
why dc is used in control circuit for mv & hv switchgear instead of ac