how we can know which is Lv side and HV side of transformer
by just seeing it?
Answer Posted / mubasher
Try to see the connected cables if you can distinguish between HV & LV cables
HV side there is only one big cable which is multi core and LV side three separate cables and neutral cable
if there are no connected cables then see the glands available for cables; at LV side there is provision of single gland and at LV side there is LV cables termination box.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
What are the ratings of VCB, MCB, MCCB, SF6, ACB, and OCB?
How will you utilise electrical power? You can start from the generating station.
why capacitive load is not used in routine life????any reason is there ??????
Define the three phase formula fuse.
i want to run 11kv star connected motor in 6.6kv with delta connected throught inverter, is it possible?
How to measure size of cable on a given load
for a 500 KVA connected load, I calculated 30% of capactor for power correction. Even after using 225 KVR capactor PF is not improving. What could be reason for low Phase correction factor?
What is the difference in calculating size of AC cables compared to calculating size of DC Cables? Usually DC Cables are larger than AC Cables although they have the same ampacity. Why is it?
what is the acceptable value of TAN DELTA and dissipation factor for 11kV, 1.75HP Motor?.
sir vizag steel ka junior trainee ka paper kitne number ka ayega
show the single line diagram of star delta starter with single phase preventer
Explain different types of d.c motors? Give their applications
What is the drawback of static coefficients?
Why corona leads to production of Ozone and glow of the color VOILET?
we are having 15kw and 3kw motor both can run in same time , instead of using copper we are using ug aluminium cable , 35 sq.mm is suitable for its current carrying capacity..?