Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

How star and delta connections inherently eliminate triplend
harmonics?

Answer Posted / raj patel

star connection eliminate multiple of 3 harmonics because of its phase sum at that point makes it zero. and same case for delta connected winding it is that phasor sum of current for multiple of 3 harmonics get zero. So without any special arrangement it is inherent capability of star and delta connection to eliminate harmonics that are multiple of 3.

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is pd controller?

1117


In electrical locomotive engines, the DC series motors is being used as traction motor. But in new engines like in WAP7 & WAG9 the 3-phase squiral cage induction motors has replaced them. So can someone tell me the advantages of induction motor over dc seris motor in engines points of view....???

2523


How colour picturetube works & how many year it will works.

2035


Direction of flow of active power and reactive power with logic?

1754


explain supply side and demand side energy management with advantages & disadvantages

2152


How grounding is different than earthings?

1165


Who are the manufacturer for Nitrogen based Fire Protectio/explosion prevention for Oil Filled Transformers? India and international both?

1924


In a Impedance Based Distance Relay (Quad Characteristics) - Could there be two different Line Angle(RCA) for Ph-Ph & Ph-Gnd? If So Kindly Let me Know.. Where, What are the advantages of the same?

1429


state types of reflectors in illumination engg. ???????

1941


Why we find the sensitivity for the CT's to check?

1867


what is meant by class 1 E in electrical power supply?

2117


what is the difference between 4pole & 6pole DC Motors & give advantage ?

1906


what is earth-fault?when it occurs? to check where it occurs what type of test should we do?

1998


TRAFO 1. WHY BREATHER IS USED. 2. WHY OIL GOES DOWN IN CONSERVATOR TANK. 3. WHY WE ARE TAKING OIL SAMPLE TAKING FROM BOTTOM OF TRANSFORMER. 4. HOW TO CHECK IR VALUE OF TRANSFORMER. 5. WHY OLTC HAVING BUCHHOLZ TRIP ONLY; WHY NO ALARM. 6. OFF LOAD TAP CHANGER OPERATION PROCEDURE. 7. TR. SHUTDOWN / ISOLATION PROCEDURE. 8. WHEN THREE TRS. IN PARALLEL, ONE TR. IS NOT SHARING THE LOAD – WHAT IS REASON AND WHAT YOU WILL DO. 9. WHY TR. HAS OLTC IN HV SIDE. 10. WHAT IS % IMPEDANCE. 11. WHY TR. RATING IN MVA. 12. WHAT IS VECTOR GROUP IN TR. 13. CONDITION FOR PARALLEL OPERATION OF TRS. 14. WHAT IS TERTIARY WINDING. WHERE IT WILL BE. 15. IF TR. TRIP ON BUCHHOLZ OR TAP CHANGER RELAY, WHAT YOU WILL DO. 16. DIFFERENCE BETWEEN OIL TEMP. AND WINDING TEMP. PROTECTION 17. HOW WINDING TEMP. IS MEASURED IN CAST RESIN TR. 18. DIFFERENT TYPES OF FAULTS IN TR. Trafo - Page-1 of 2 19. WHAT HAPPENS WHEN TR. CHARGED FROM LV. 20. WHAT WILL YOU DO IF MEGGER READING SHOWS ZERO BETWEEN LV WINDING AND EARTH. 21. CAN WE INTERCHANGE BUCHHOLZ RELAY OF MAIN TANK AND OLTC TANK. 22. IF THE LINE BETWEEN BREATHER AND CONSERVATOR TANK 23. LOCKED, WHAT WILL HAPPEN DURING LOAD CYCLE. 24. WHAT IS THE FUNCTION OF OIL SEAL IN BREATHER. 25. WHAT ARE LOCATIONS FOR BUCHHOLZ RELAY FIXED IN POWER TR. 26. WHAT ARE CHECKS IN POWER TR. DURING MAINTENANCE. 27. WHAT IS IMPORTANT WHEN WE CHECK OLTC OPERATION DURING MAINTENANCE. Trafo - Page 2 of 2

2399


Is there any specialised book to refer about fault level calculation both in MV and LV side??

2071