A 200W,230V lamp is connected across 115V supply.The lamp will
draw power?
Answer Posted / sachin prajapati
(1) R=V1^2/P=230^2/200=264.5
V2=115
P=V2^2/R=115^2/264.5=50W
(2) R=264.5
I2=V2/R=115/264.5=0.435
P=V2I2=115×0.435=50.025W
So answer can both
| Is This Answer Correct ? | 6 Yes | 5 No |
Post New Answer View All Answers
what is the standard duration after failure EB power
2- What are the percentages between excitation currents in phase (R, S and T) in ∆ and Ỵ connections in excitation Current test in transformers?
What is the voltage gain or transfer function of amplifier?
give me applications of sequence bridges . (used in 3 phase un balanced systems)
Mention the disadvantages of low power factor?
how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)
what is the difference between switchgear and circuit breakers and is there any difference between outdoor and indoor switchgear and circuit breakers , and how would you differentiate between switch yard and substation and grid station . thanks
how can i determine the gear ratio for a rack and pinion system if an electronic gate operated by an electric motor is to travel a distance of 5meters in 15 seconds.
How the frame size of a flange mounted AC induction motor is calculated?
In how we connect watt meter for open & short circuit test of a single phase transformer.
Why squirrel cage motor can only use with low starting loads ?
What happens if we run alternator on under frequency?
Under wat condition statcom operates as an inductor for the transmission line?
what about GD square and its important for motor design?
How to calculate earth fault current for 6.6 KV , 50 HZ , 756 Amps , 3000 RPM , 0.8 PF generator