How CT is connected to measure current by changing plug setting , ratio is 300 - 150 / 5 A ?
Answer Posted / ravi patel
Plug setting of a relay is the setting of a relay pick up current.
A relay pick up current is defined as the value of current through relay coil at which relay starts to operate.
Generally, it is specified as percentage of relay pick up current.
A relay plug setting (PS) have a value in the given range i.e. 50 to 200% .
Plug setting of 50% means as soon as current through relay coil increases above half (50%) of relay pick up current, it will start to operate.
Similarly, Plug setting of 200% means as soon as current through relay coil increases above two times (200%) the relay pick up current, it will start to operate.
If CT ratio is 300 / 5 A ,
then Relay pick up current (Ip) = 5 A
Thus,
If PS = 100% ,then Ip = 5 A corresponding secondary current = 300 A.
If PS = 50% ,then Ip = 2.5 A corresponding secondary current = 150 A.
If PS = 200% ,then Ip = 10 A corresponding secondary current = 600 A.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
Why temperature rise is conducted in bus bars and isolators?
Convert a star connected network into a delta connected network.
Earth leakage relay basic knowledge principle
what is frequency response?
How to calculate the value of earth capacitance in a transmission line.
I am doing apprenticeship training at HT switch yard in NLC. How can i get electrical c license. ??? What r the rules for getting it as an apprentice? ??
what is the pulse and audio frequency transformer? what is different between induction regulators and tap changing transformer?
how is working bearing heater?
IN induction motor pf is increased using capacitors.what will be the effect on motor and system when very large capacitor is accidently installed and pf goes leading.
How Can you do Maintenance of ACB of 2000Amperes
how power trnafor from 1 point to another point in bus bar ya transmission line( voltage trnasfer from 1 point to another poin)
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
"TRANSFORMER MODELING AND ANALYSIS" MEANS WHAT AND WHICH TOPICS U READ IN THIS
In siemens S7-300 PLC, what is function and function block ? What is the difference between them ? When to use function and when to use function block ?
How do the synchronizing lamps indicate the correctness of phase sequence between existing and incoming alternators?