Is there any particular formula for sizing the bus bar based on the current rating
Answer Posted / krishna kumara shetty
A= ((sqrt i^2)*t)/ k ......?
Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
The D.C. spark test is applicable to single conductor cable & assemblies of insulated single conductor cables without insulation shield,metallic sheath or metalic armor?
Difference between ac parallel circuit and ac series circuit?
List the disadvantages of constant k filters?
How to control motor gearbox speed and friquency? If length of cable and dia given, how to measure the voltage drop?
Why do we need interlocking in a HT metering or Ring main unit switchgear?
What will be the output voltage of a transformer if it is primarily energized from a square wave voltage source?
What is CCM in Electrical ? where can we use this material?
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value
What will happen if the armature resistance is in minimum position and the field resistance is in maximum position while starting the motor
Why the output of OP-AMP is always less than Vcc?
what is the Transformer Impedence?How can calculate?
After synchronization with grid what is the demand value QKVAR and how we will maintain that?
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
Draw transformer phasor diagram.(full load,no load)