What is the difference between instrument earthing and normal earthing? and why is it necessary to do so?
Answer Posted / mugil
Instrument Earth:
Instrument Earth is also called as Reference earth.Instrument Earth all individual shields(Screen) and
over all shields single or multi pair cable shall be isolated from electrical earthing due to avoiding interference and terminated different bus bar.
Instrument bus bar will be connected to grounding dispatcher by 25 sqmm green- yellow cable.Grounding dispatcher to earth pit is connected to 70 sqmm green -yellow cable.
Electrical Earth:
Electrical earthing also called as dirty earth or protective earth.It is used to protect the power system,electrical equipment and personnel from electric shock.
| Is This Answer Correct ? | 17 Yes | 3 No |
Post New Answer View All Answers
what is function of switch, and how is it work, explain with difination
Draw a wheatstone bridge circuit showing supply, meter and 3 wire RTD connection
how many pulses are required by a ac induction servo motor of 4 poles with 50 Hz frequency to rotate by 1 degree?
can any one tell me when ongc placement test and its forms is available????/ pls tell me if u know
What are the error values can accepted in flow transmitter calibration?could u give any formula for this?
Somebody can explain me about >Critical Loops, calibrations, ESD critical Loop checks, Logic Diagram / Cause & Effect checks for ESD loops,
What denotes the 5/8mm in the 3300XL 5/8mm proximitor probe?
Explain PID, ON/OFF, Controls
please tel me the calibration of pneumatic controler.
hye SAM acn u send your e mail id, so that i can solve my query through e mail?
Please can anybody help for control valve sizing step by step procedure?
why we are using magnet for calibration of gas detector?
Describe the functions of the Operator Interface including the considerations related to alarming and display layout/configuration/layers.
How to calibrate displacer type level transmitter (chemtrol make )for level measurement in hotwell , LP & HP heater ?
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.