A 200W,230V lamp is connected across 115V supply.The lamp will
draw power?
Answer Posted / tripti kumari
first we find the resistance of the lamp that is given by formula p=V*V/R
R=230*230/200=264.5 ohm
now current flow through the lamp when connected to the supply 115 V that is
I=V/R
I=115/264.5=0.435
now power draw by the lamp given by
p=V*I=115*0.435=50.025
so it is slightly more than 50 W.
Is This Answer Correct ? | 95 Yes | 45 No |
Post New Answer View All Answers
Differnce between negative Pahse SequenceFunction and unbalance Function?
why various test are performed on electrical panels & power cables before commissioning on site & what are these test???
HOW TO CALCULATE EARTHING SIZING?
what is earth fault relay 64T, why it is used in main Incomer and neutral CT of Transformer.
what is the use of static frequency converter and static excitation equipment? and where it is employed? for what?
why do we carry out winding resistance test?
What is the accepted limit to increase the choosen transformer capacity over the load and why ?
i want to know that what is the eligibility critaria for ongc exam?
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
wat is d diffr btw shunt coil and trip coil in VCB?
What do you mean by an instrument transformer?
what is the difference between interconnection and intraconnections in the circuit diagrams
Explain what is electric traction? Explain few advantages of electric traction system?
how does grading rings & spacers in transmission line works? Working Principle?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box