how to calculate knee point voltage of current transformer?

Answer Posted / rajkumar

Knee Point Voltage Vk = IFsc * K * (Rct+(2*RL)+Rr)
Where,
IFsc - Fault current at the secondary of CT
IFsc->IFprimary/CT Ratio
IFprimary -> Fault MVA at primary/(1.732*Primary Voltage)
K - Dimensioning Factor
Rct - CT Resistance
RL - Lead Resistance
Rr - Resistance of relay to which CT is connected

Knee point voltage is the voltage at which 10% raise in secondary voltage will result in 50% raise in current..

Is This Answer Correct ?    2 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Grid fault level [KA]?

2204


what are the advantages disadvantages of connecting high voltage block( 1:1 transformers) transformers between the turbo generators and busbars.

1667


how circuit breaker work.. what is the operations taking place inside a circuit breaker when an overcurrent occurs... is it similar to fuse?

1616


Explain about technical and non technical losses in distribution system?

623


Name the test signals used in control system

796






salam&hi, i need to know about how can i calculate an enough current for the new building before i submit it to the suppliers

1614


What is the principal of motor?

648


What is the type of earth fault protection used in battery? explain.

1858


Why does curving the pole faces in a dc machine contributes to a smoother dc output voltage from it?

764


after how many spot we must chang secondry cable in portable spot welding gun?

1463


What is the breaking capacity of transformer and how can we calculate the breaking capacity of tranformer

1250


I am inpecting a 10kVA UPS what tests should i do and should i observe?

1799


what are the different kind of cables used for transmissions?

719


1- What is the Polarization Index number be good for 15KV 3c#500MCM electrical cable? 2- Can I use the IEEE Std 43-2000 to perfom the PI test? Thanks

2911


what is the use of permanent magnet generator in exciter

1693