What is working principle of ACB and VCB?
Answer Posted / gomez jerald
An ACB Is constructed for a particular contact rating at medium voltage .Technical explanation the contacts energize and d energize the arcing air medium during the process is quenched in an open chamber.
VCB is constructed especially for higher rating voltage and the technical term .the arcing during energizing and d energizing is quenched in closed chamber at very low pressure.
| Is This Answer Correct ? | 8 Yes | 0 No |
Post New Answer View All Answers
What are the three types of compensators?
how to know the diffrential relay setting of 06mva step- down (delta-star)transformer?
i have a 4 Mva transformer 34.5 kv / 480-277 v and i used 2 parallel 3200 amp bus duct for the secondary feeder using 3 ply of bus bar ( 3/8" x 5" ) as a common where the flexible link terminated and 6300 amps breaker for the main, the lower bus duct reaches 70 degrees and the upper bus duct reaches 55 degrees when i used thermal scanner. why the temperature is not balance when the load reaches 3600 amps.
Define conversion efficiency of a power amplifier. What is its value for class c power amplifier?
How can I calculate ISF of current transformer?
What is a dc motor?
for 100 HP Induction motor service factor is 1.2(SF) we placed a VFD at the motor side load is balance with 0.3 Amp's Phase to Phase but at incoming of VFD load is un-balance with 10 to 20 Amp's what will be cause of load un balance
What are different types of control systems?
how does high earth to neutral voltage affect electronic equipment?
In general bus riser follows the bus section in SWGR. What are impacts if bus section follows bus riser?
HOW DO YOU CAN CHECK A 15KV DIODE, WHETHER IT IS OK OR NOT?
Why to keep capacitor bank off while generator running.
Brushes are placed at magnetically neutral axis,when brushes reach that point,the armature conductor gets shorted,but it can be seen that the dc supply is also shorted,wont that get damage? help me plz
what is kvarh? Please define it With calculation General motors ?
How to choose the vector group for the step up and step down transformers??? Tell me the which vector group is suitable for step up and step down transformers and whats the reason to choose and whats the benefits???