What is the main difference between power transformer and
Distribution transformer?
Answer Posted / pushparaj
Distribution Transformer are Output LT supply and power transformer are HT/HT step Down/Up.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
why the electrolyte level in lead acid battery is maintained 2.5 cms above electrodes?
l&t switch FN 63 handle position can we change
what are the preventive maintanance actions taken for air circuit breaker? please answer me
sir& friends i want the collection of recent quetions asked in interview of top most companies please send me on my email san.jsr@hotmail.com
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
How to confirm the Phase shifting Transformer VECTOR GROUP relation , as below ZNy11.45d10.45-ZNYy0.15d11.15
what should be the acceptrd value of winding resistance for 2.5MVA transformer
Draw the line diagram of diffretial relay connected to transformer?
Can clean earth cable be considered as low current cable
what is current check gurd relay?
how to discharge 3 phase power factor correction capacitors
why connecting surge unit in contactor coil
why the active power flow of some line is increased when the active power of out is cut ?
bsec exam syllabus (mis)
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes