I need to calculate the Battery bank back up for below configuration:-
UPS - 120 KVA
Battery Bank - 200Ah
Volt of each cell - 12 V
Total No of cell - 34 No's
Can you please help me to get the battery back up time for above configuration...? along with formula

Answer Posted / k.prakashchandra

Energy stored in each battery = 12 x 200 WH ( VAH) ,total stored energy = 12 x 200 x 34 WH . Divide this by load in W to get ' Back up time' in hours (approx)

Is This Answer Correct ?    0 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How can we calculate ac current from the given DC current when AC voltage is given?

1539


design of IGBT firing circuit for 11KV

2107


how  do you choose the cable size as per amps rating & the voltage drop for the same.

1342


What is difference between Sample test and Routine test in safety standard?

1296


how to determine the cable size...pls explain me with the formula taking particular load....does the factors like impedance & short circuit rating influence the cable size, if so how....

1583






Why using synchronising methed in DG's sets?

1728


IF DISTANCE IS 100METERS B/W AMP.METER AND CURRENT TRANSFORMER WHAT WILL BE AFFECT IN ACCURACY .METER CAN SHOWING ACCURATE CURRENT OR NOT IF NOT WHAT CAN I DO TO GET 100% ACCURACY.

1424


is this the formula of building wiring to get the main breaker.Watts/volts*.8%+higher motor*(25%)=ampere. yes or no or send the correct formula for building wiring.

1181


Sir, My doubt on cable sizing calculation, Load:74 KW calculated cable 1 run 50mm2. Now client asking us to reduce cable size by increasing runs. Sir, My question now when my mind strikes with 2 options 1) Divide load 74/2 = 36 and calculate cable for 36+36 making it 2 runs or 2) Simply i can divide 50mm2 /2 ie. 2 runs of 25mm2 Please suggest me sir

1435


dear all i am kumara now current working in electrical designing of control and relay panel i want learn some substaion design then any book are available. pls mention name and authour

1516


While performing stability test of differintial cts how to know the voltage and current on both side of the transformer?

3072


Hi guys! Plz help me to answer the following questions. 1. What are the types of transmission line energy losses? 2. Why are the VLF are used some types of services? 3. What frequencies are used for reliable beyond the horizon terrestrial communication without repeaters? 4. To permit selection of 1 out 16 equi-probable, what is the number of bitis required? 5. What is the most common modulation used for telegraphy? 6. What is the multiplexing is used to increase the capacity of the optic fiber? Thanks

1628


How to findout raw or ups power? its not indicated in socket,

1550


with 3 phase board on a 63 amp rcd is it ok to have 6 electrical showers 2 on each phase and what problems could happen

1406


In what condition the HT fuse breakes?

1497