what is the difference between synchronization and paralleling?
Answer Posted / bhagavatsinh
synchronization is the process where voltage , frequecy, and phase angle must be same. but in parelleling it differ in acceptable tolerance. I.e. you can parrellel a two transformer which have a voltage 11kv and 11.5 kv and freguency 49.80 Hz and freguency 50.20Hz and phase angle according to vector group
| Is This Answer Correct ? | 0 Yes | 2 No |
Post New Answer View All Answers
Explain mechanical rotational system?
What is difference between Over Current & Earth Fault protection?
How to check the cable fault / hv test of transformer cable.
which connection is safer series or parallel?usually which connection we prefer at home?
WHAT IS counter flux IN CT?
what is alluminium arm in ab conductors
what should be correct gas pressures to be a 1.5 ac unite
From past few months I am getting lagging pf even though sufficient capacitors used in circuit. Where is the problem pls answer
sir, what is the importance of Fault MVA. how to calculate fault mva of 33kv substation connected by 6.5 km line(single circuit with equal spacing) with 110/11kv transformer in 110kv susbstation.the fault mva on 11 kv bus in 110kv susbstation is 208mva.
What is the actual calculation for transformer short circuit test?.
what is LSR?
From reading, Under voltage relay used also as phase sequence relay now, Why I use under voltage and phase sequence relay in the same circuit (ATS)?
Pleae send me last 5 years of Question book about RRB chennai.
What is the use of oil in transformers?
How to Decide(calculate) Bush bar size for copper and aluminiam ?