how much amp MCB is required for 1/2 kva power back up?
Answer Posted / vicky
1KVA = 1000VA
Therefore 1/2 Kva = 500va
For a single phase current
500/230=2.174
So the MCB you can put here is a 2.5AMP as it will not be possible to get a exact 2.174amp MCB
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
why single phase to grd test in HV cable?why not 2 phase at a time?
2 v/500amp/hr to 1.80vpc at 20 degree celsious 2v/5ooamp/hr to 1.75 vpc at 77degree farren .this is the capacity of a battery .what is the meaning of this . can i get a detailed explenation
What is the formula to find out two phase active & reactive power
When and where resistance earthing is used ? How to calculate the time constant for earth fault
In DC generator, we use commutator, having no. of segments. Then how it is possible to get a half wave of voltage and current for half rotation of armature?
Whether IP65 enclosure box blocks ventilation if driver for LED have to enclosed inside IP65 box
List advantges of active filter over passive filter?
What is the difference between a verilog task and a verilog function?
Explain the construction of the conservator, operation and purpose, and draw the diagram of the conservator.
what happen if drive input fail momentry at 48.5 HZ frequency?
what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)
what is the criteria for selecting fuse rating in 1phase, 2phase & 3phase welding sets?
Single line diagrams for star to delta and DOL starters.
How to do fabrication , busbar and wiring cost for : 1. LT Panels 2. C& R Panel
Merits & Demarits of Oil circuit & Air circuit breakers ?