Can someone explain how does an IDMT relay works.
Answer Posted / poorvalingam
Its also called inverse relay. consider disk type induction relay. you set the over current setting 70% means this disk will pickup above this setting.consider if 85% of load going the disk will rotate and trip the circuit. if the load is 110% that time the disk operate very soon then previous case, it trip very quickly.
The operating time inversely proportional to the fault current this type relay called Inverse Definite Minimum Time Lag relay (IDMT)
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
Why generation voltage in thermal power plant is between 11kv to 33kv?
what is the ground fault relay,which purpose it will be use,clearly tell me plz
what is cathodic protection and why it use in industries?
how to select the double earth conductor if 21A full load?
what is JE exam?
why we permissive overreach in distance protection.where it is applicable to use in long r short lines
How to calculate or formula to calculate rhe power in 2 phase system ??
Why do we pefer VCB over OCB?What are the advantages of VCB over OCB?
How to do cable earhing? whether by grounding Armour to ground or by running extra G.I wire along with cable? which one is preferred mostly amoung them? If the second one is more preferable how many GI wires to be run along with cable (1 or 2)?
How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me
why zero sequence impedance measurement is not applicable for single phase GT
what is the main parts of transformer? how it is functioning? pls giv the ans briefly.
what are factors to be consider in electrical installation like load factor,diversity factor .....
what happens when dc generator coupled with cycle shaft.also explain what happens when its loaded
how to identify vector group of three phase transformer by voltage method?