What is the meaning of burden and class of accuracy of CT?
Answer Posted / poorvalingam
1.Burden is the actual load can handle by the C.T in (KVA)
Eg: the C.T need to operate the relay for fault tripping if the relay has 12 Va means the C.T burden must be greater than the relay load to over come the cable loss. it may be 15 va C.T enough
2.Accuracy class means , it says the % Errorof the C.T from no load to 120% of load for metering purpose and above the full load current for Protection C.T
Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
typically in power distribution substation. 1- Any idea how would be the graph of capacitor bank consumption verses time through the day . 2- How is the switching ( on and off ) of the capacitor bank, per need?
How delta connection in the primary of distribution transformer reduces harmonics?how delta connections reduces harmonics?Please answer me...Hope that question is correct.
What is CVT and what is relation with wave trap?
how did i get the competency certificate as electricle supervisor. iam completed my b.tech.but i dnt have any experince, this certificate is required for applyng ongc mangement trainees. what should i do sir please suggested me
What is diversity factor in electric installations?
what is servo motor and how it works?
what will happen if the prime mover on the field excitation of the on-coming generator fails?Explain.
What is the difference between the impedance percent and impedance voltage ?
What are the main parts of central chiller plant? Explain the function of each stage.
list the advantages of RCCB over other circuit breakers?
Define noise?
What is mean by hot and cold loop testing?
Pls Breifly explain about UPS (Inverter,Reserve,Rectifier,Float voltage,Boost voltage).
what is relation between ct and pt ratio with multiplication factor of a energy meter? is there any other factor on which multification factor depend?
what are the analog quality input for protection function?what are minimum reqiments?