What is difference between earth leakage relay and
restricted earth fault relay ?
Answer Posted / narottam pradhan
The relay which protect the equipment/system by disconnecting supply when a earth fault occures in direct grounded system of power supply is called earth fault relay.In case of restricted earth fault relay the magnitude of earth fault current is limited to a specified value by employing suitable designed restricted neutral system of power supply.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
How to calculate wire length,size & current? ( related to control panel)
what is the effect of back reactive power on the generator ?
Why does curving the pole faces in a dc machine contributes to a smoother dc output voltage from it?
Meter p.t. ratio= 3×230/400 , c.t.ratio = 3×1 (2) A what is m.f.
how do i work out the Amps of a incommer if i am running 1 37 KW motor and a 0,75 KW motor and some solinoids
two way ckt diagram can be drawn by how many ways? give diagram
How to calculate the sag on transmission Lines.
How many capacitors using in LT panel as per Govt rules?
we have earthmat at 110KV substation.we would like to take earth resistance.b some says that by connecting earth megger terminals (C1,P1) at middile point of earthmat (at riser) will cause voltage gradient at other earthmat nods and dont get exat earth resistance.when connecting at end nods will get exat value . is it correct .please explain
how to select battery for 15 KVA UPS with formula
What is frantic effect?
what happens to the supply voltage if there is any change in frequency?
How do we calculate transformer oil in liter from the rating of the transformer.
What will be the diameter of pipe between conservation tank and transformer
What is the power factor of a transformer at no load?