In which connection the voltage will be more , in star or
delta connected motor?
Answer Posted / mohammed rafi
all aforesaid answers are absurd or partially mistake.
Both delta connection and star connection has same voltage.
But star connection gives the provision to tap a separate single phase connection which will be of course lower voltage.
For example- In India,existing 3 Phase supply is 415V (10% deflection is permitted). You can obtain it either in the form of delta connection or star connection.
The single phase connection (230 V)which you receive in your home is actually a taped connection taken from star connection. A star connection will have 4 wires,there are R phase,Y Phase, B Phase and Neutral. Voltage between R-Y and R-B and Y-B or any phase to phase combination is 415 V
Now if you take a phase,let it be R or Y or B and check it's voltage w.r.t neutral,it will be 230 V. This is known as single phase voltage.
Delta connection has only 3 wires,they're R,Y,B and there is no neutral. So You cant tap a single phase from a delta connection directly.
This is the difference between star and delta connections. Moreover its worth to mention that question which triggered all these discussion is wrong. Because,now you have understood both has same voltage but the only difference is you can tap a single phase connection from a star connected supply.
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
what about the power of wattmeter at starting and loding?
Why do we need a separate control desk & PLC control panel in Boiler plant or coal handling plant? Can we provide cost effective Control desk cum PLC panel. Is there is an specific need for control desk.. kindly advice.
what is mean by NPS (Negative phase sequence)fault? what is the difference between EFR & OCR faults?
What is the Difference between Ac Drives and Dc Drives? According to application, speed, Torque, cost, Reliability, Construction, Motor etc... Thankyou !!!
WHAT IS counter flux IN CT?
What happens to voltage when current through the inductor is constant?
How to select batteries required for ups and the inverter if we Known load? And how AH is selected of battery?
what is the function of impulse relay
what will happen if synchronous machine rotor fed from single phase ac supply
explain why core loss of a transformer is almost constant under different load conditions when connected across a constant voltage and constant frequency.
If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma
how we calculate torque ? how we improve it ?where torque will either motor or generator ?
where solid grounding and where grounding through ngr done and why?
How many wall/floor flange will i use in bus duct system if we have in our design a 35th floor building.
When will you multiply and devide with derating factors to the actual value while sizing the cable?