what is RTD? what is THERMOCOUPLE? What is difference between
it?
Answer Posted / tamjid
RTD is cheaper than thermocouple, and TC is more accurate than RTD, we use RTD for temp sensing bello 150C, but TC used for high temp sensing,
| Is This Answer Correct ? | 1 Yes | 0 No |
Post New Answer View All Answers
How can we findout the maximum efficiancy of Transformer? At which load?
If the rated speed of a d.c. Shunt motor is1440 r.p.m, which method of speed control would you suggested to obtain a speed of 1500 r.p.m?
how to decide no of electrodes for 1600A LT Main incomer panel
how to calculate slip ring induction motor stator and rotor currents??
What happen in ups if phase reverse?
What is PEC??Applications........
What is the comparison of PILC and XLPE cable
What is the reason for using a GE G101 MCB in place of an EP102 MCB if both are capable of AC circuit protection?
how we sesign the transformer give some specifion regarding design of transformers
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
What is the difference between diode and a transistor in terms of the direction of current flow?
what is counter poise conductors
what is feeder bay?
What is the effect of positive feedback on stability of the system?
Why does inductive loads consume KVARs?