Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

Why we use 250 ohm resistor in series with HART protocol
communication?

Answer Posted / mahalingam

The 250-ohm resistor is not placed in the loop for the idea of converting the current (4-20mA)from transmission to voltage (1-5V)for reception, and also the value 250 is not a special value for a loop resistance needed for HART communication.

Explaining first the true purpose of having a resistor in the loop:

The HART communicator is communicating with the transmitter through FSK protocol. Understanding this protocol, it is a communication in analog platform. Digitalization of the signal happens within the HART devices and not along the transmission line.

The resistor's position in the loop is between the transmitter and the DC power supply. As we connect the communicator it should be tap between the resistor and the transmitter or directly parallel to the resistor. Why? Because the power supply has a LOW PASS CAPACITOR filter that basically squelches analog signals like ripples. Thus, if there is no resistance in between the PS and the TX that analog signal coming from the HART devices will only be filtered out.

Explaining the value 250:

The resistance value is not necessarily be 250 ohms. Maybe because of the idea that the controlling current of 20mA will give us 5 volt calibration if there is a loop resistance of 250 ohms. Maybe not a good theory.

Actually you can use a number of possible resistance values that will allow communication between HART devices. This value depends on the transmitter minimum operating voltage requirement. Simple OHM's LAW. For example, if the voltage requirement for a certain transmitter is 12-24 volts use a resistor that will not give you a drop of below 12 volts or else you will not deliver power to your transmitter. Most transmitters are supplied with 24 volts and as per computation 250 ohms to 500 ohms gives a drop of almost 18 v which is somewhat in between the operating voltage

Is This Answer Correct ?    13 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

How to interfacing microcontroller with a DC motor

2045


what is the minimum power (P=VI)to produce a spark?

1971


how to calibrate load cell

2828


1. what is modbus cable? 2. what kind of communication we are using for the interface of DCS, ESD and Third party cabinets? 3. What is serial communication and peer to peer communication?

2186


Explain Gas Turbine startup and shutdown sequences

4310


we are having yokogawa centum cs3000 dcs in our power plant. i need some of the operator guides NOT to appear in HIS0163 AND HIS 0162 but it shoul appear in HIS0164 HOW TO DO IT?

2573


Give an example where you had aproblem on the job, and tell me how you solved the problem. and the finalvoutcome.

2236


What are advantages and disadvantage of the ac supply load cell?

1041


in which principle pressure tx,level tx ,flow tx,temp tx ,control valve works?

3158


How to calibrate the flow transmitter

1605


what is isloted barrier how it works and what are the main purpose.how it make safe area.

2120


How to Calibrate Temperature Switch in field

1308


what is the field bus calble ? what are diffrences in orang colur cable and black coular calble ?

3004


What is mean by analytical instrumentation?

1810


how to tune siemens sipart electro pneumatic positioner..plz tel me..

2125