What is the working of AVR in AC generators?
Answer Posted / rakesh
The function of the AVR is to automatically regulate the voltage of generators. As a load on a generator increases it's terminal voltage tends to droop.The AVR senses the drop in terminal voltage by measuring the generator voltage and boosts up the excitation to the field of the generator to maintain the terminal voltage at the set level.Similarly as the load on the generator falls, the terminal voltage is maintained by the AVR by reducing the excitation to the field.
Is This Answer Correct ? | 19 Yes | 1 No |
Post New Answer View All Answers
as a electrical student why should i hire you?
what is load despatching
Difference between transition and diffusion capacitance
The specific heats of the gas at constant pressure and constant volume are respectively 1.0 kJ/kg K and 0.72 kJ/kg K; the value of R for the gas is
What descriptive information does the NEC require to be marked on all conductors?
What is inductance?
Can I use distributon class/transmission class Lightning arresots for protecting the building? If not why please explain?
There are a trformer and an induction machine. Those two have the same supply. For which device the load current will be maximum? And why?
How do we calculate transformer oil in liter from the rating of the transformer.
what is is the potential diffrence between two phase ?
Explain about retrofitting of machine tool.
What Is Connection APFC Panel In Compony.
Why front mounted CT polarities are always towards breaker?
Y phase plates are used in transmission line??? what is there need???
Is it required to lay 2 runs of GI wires along with armoured cables from one power DB to another Power DB?