Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

What is OLTC in a transformer, specify its fuction.

Answer Posted / raj lahare

Dear Dnyaneshwar, Please mote that 1)In HV transformers the LV winding is nearer to core and the HV winding is away from Core There fore it is easy for taking the taps .2) The current in HV being lower the switching current in OLTC is low.
Please note. 3)The RTCC means the Remote Tap Change Control Cubical This is installed in Control Room so that the Taps of the Transformer which is installed in Switch Yard can be changed from the Control room only. 4)The RTCC if provided with AVRCR then the taps are changed automatically by sensing the LV voltage. The AVRCR means AUTOMATIC VOLTAGE CORRECTION RELAY. 5) In bigger transformers say Voltage class 220 KV and above the OLTC tap connections are provided on LV side due to the insulation levels of high voltages at the switch.

Is This Answer Correct ?    0 Yes 1 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is nichols chart?

1336


1.WHAT IS A SMART CAPABLE DB ( DISTRIBUTION BOX) ? 2. HOW TO DECIDE THE TYPE OF DB TO BE USED ( RECESSED/ PLUG TYPE/ SMART ETC ETC? 3. WHAT IS MILLENEUM BUS BAR USED IN DB? 4.DIFFERENTIATE MCCB AND MCB.

1850


what is laser diodes?

1167


how indusrial diesel generator work

1926


What is the difference between amorphous core transformer and CRGO core transformer?.

3744


what is mean by kneepoint voltage? when it will happen? ( my doubt is, if CT secondary is open means ct get saturation or blas? what are factors are required for calculations? plz give currect anws:

2037


Control wiring of a dol starter for forward and backward

1587


how to calculate the earth fault current

2507


Can anyone please provide me details of MCCB/Contactor/SFU rating calculations for a motor feeder..for example 50 kw.. not from type-2 cordination chart. i want manual calculations..

2595


hello if any one have papers vof hpcl or sail, plz send me

1928


can any tell me why slope 40% and 80% is calculated in differential protection?

1892


If I have 3 essential main switch board and 3 incoming electricity ,but only 1 genset running is that possible.

1642


1. What is differential relay? How it operates? 2.How to calculate the Short Circuit Impedance in Transformer? 3.What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works? 4. While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply? 5. What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer? 6. Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example? 7. Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient? 8. What should be the minimum and maximum ohmic value for earthing? 9. Why DC Currents are not used in transformer? 10. What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?

2280


Why do we perform an open-circuit test and short-circuit test on the transformer?

1124


explain the function of brush less dc motor?

2100