Give a brief idea about Control circuit wiring in
Substation...???
Answer Posted / waseem aslam
Control circuit wiring of substation refers to wiring of protection relays of transformer with the circuit breaker and wiring of over-current/earth-fault protection relay in the CB, including manual tripping operation.
| Is This Answer Correct ? | 0 Yes | 0 No |
Post New Answer View All Answers
why steady state stability limit is greater than transient stability limit ? How it can be explained ?
WHAT IS THE FORMULA FOR CALCULATING CURRENT RATING(DIRECT IN GROUND OR AIR) OF ARMOURED(XLPE) CABLE OF 4C,16Sqmm?
how to find the multiplication factor for digital energy meter and analog energy meter
CALCULATE THE TOTAL VOLTAGE DROP AND SELECT THE CABLE SIZE IN MM-SQARE FOR A PANEL-262KW AT 110 METER FROM THE SOURCE SUPPLY , SUPPLY VOLTAGE 240/415
ANY ONE TELL ME ABOUT generator synchronization panel panel to synchronise 3 gen of 250kva both automatic and manual. 2 gen output vol 415 3ph, 1 gen output vol 400 3ph SEND THE DETAILS DIAGRAM ON THIS EMAIL ADDRESS ayazleo@hotmail.com as soon as possilble best ragrds electrical engineer ayaz mahmood SAUDI TECH
What do you mean by Frame 5 Gas Turbine as well as Mark II.
what is die electric strnth of transformer ?
how to select fuse rating for a 3-phase motor ???
What is magneto on a gas generator. how it functions. its out put is d.c or a.c. how it can be checked for correct functioning
What is a surge supressor why its is used in synchronous generators
How i can decide that HVDC line is best for transmission.
Define thermal resistance in the context of power amplifier.
What is the Diff. btw Manule Pull Station & Manule Abort Station Switches used in FM200 System??
when ID fan will immediately stop through VFD what exactly cause and problem the ID fan
What can you contribute to the progress of our Company as an employee if you are selected?