what is the formula to get the 3 phase motor winding resistance? for example, i have 460v and 3A ? what would be the per phase winding resistance? thank you..
Answer Posted / ahmad raza
In your case firstly mention whether the
motor winding is in star or delta.however
firstly u need to calculate per phase
impedance i.e. per phase voltage divided by
per phase current. Then the answer u get will
be in a complex form i.e. R+jX were R is per
phase resistance of motor winding.
Example: (460/_0)÷(1.73x3)= 88.527ohm. (For
star winding)
For delta simply divide 460 by per phase
current.
| Is This Answer Correct ? | 2 Yes | 0 No |
Post New Answer View All Answers
Can any One Help me to Know about Fire hydrant and its related water Pressures
how the calculation of faut current level
What causes little rust pockets to pop through or off concrete cylinder blocks (home)?
Why normally we don’t use relay for digital input module?
Distance to be maximum distance we can install instruments from PLC panel?
What is quality management system?
Can you calibrate, troubleshoot and repair instruments? Which tools do you use for the same?
I have got an interview for a higher apprenticeship at JCB next week, the interview process consists of group and solo tasks, and group and solo interviews. Has anyone got any information in what I should expect on the day, or the frequently asked questions so I can get a head start.
What is producser for Anti collosion protection for DUMER 220Ton in Minse
On what bases time study methods can be calculated?
Define operation time?
why we give dedusting steam in feed gas coils in convection section of primary reformer?
What is plant organization?
Why control valves are hunting on manual mode?
ANY ONE USED/INTERFACED CITECT VERSION 6.0/1 OR 7.0/1 TO SIEMENS S7-300 OR S7-400 CONTROLLER IF PLEASE TELL ME THE COMMUNICATION STRUCTURE AND ADDRESS CONSIDERATION FOR DI,DO,AI,AO please mail the details lok_pallapolu@yahoo.com Ph:09247513753 hyderabad