what is the formula to get the 3 phase motor winding resistance? for example, i have 460v and 3A ? what would be the per phase winding resistance? thank you..

Answer Posted / ahmad raza

In your case firstly mention whether the
motor winding is in star or delta.however
firstly u need to calculate per phase
impedance i.e. per phase voltage divided by
per phase current. Then the answer u get will
be in a complex form i.e. R+jX were R is per
phase resistance of motor winding.

Example: (460/_0)÷(1.73x3)= 88.527ohm. (For
star winding)
For delta simply divide 460 by per phase
current.

Is This Answer Correct ?    3 Yes 0 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Let’s say we live in a country that gets very cold, in Northern America / Europe. In winter, we monitor the ouside temperature, so that heaters can be switched on, inside the house. The idea is that, the colder it is outside, the warmer it should be inside. The heating side of things is just a heater that is either switched on, or switched off. Just from the information that has been given, please discuss this matter in depth. Provide reference to OPEN / CLOSED loop control, FEEDFORWARD / FEEDBACK control and MODULATING / ON_OFF control raised in the discussion.

1053


On what bases time study methods can be calculated?

597


What is alpha test in alumina powder?

1479


how the calculation of faut current level

2207


why data registers are needed in PLC ?

2212






What is refrigeration cycle of HVAC .

1008


What is difference between npn & pnp sensors?

581


ANY ONE USED/INTERFACED CITECT VERSION 6.0/1 OR 7.0/1 TO SIEMENS S7-300 OR S7-400 CONTROLLER IF PLEASE TELL ME THE COMMUNICATION STRUCTURE AND ADDRESS CONSIDERATION FOR DI,DO,AI,AO please mail the details lok_pallapolu@yahoo.com Ph:09247513753 hyderabad

1654


What is autofacturing?

643


Explain overhauling stopsfor backpull our pumps?

1752


if zero ohm is not adjusted on shorting the two terminal of multimeter what does it indicate

1600


for the steam temp 420dec de superated to 120deg how much of water required

1573


Where do you see after 5 years

1034


How we install and terminate the wire of pressure transmitter and temprature transmitter. Give full explanation.

1000


what is difference between an encoder & resolver?

2448